I was asked to give a review of one of my EVSEs (Electric Vehicle Supply Equipment), more commonly known as a “charger.” Some pedants care if you call it a charger and not an EVSE. Technically, for power coming from a wall outlet in the form of alternating current (AC), the “charger” is built into the car and the EVSE tells the car’s charger how much current at what voltage it is allowed to pull. Nobody except those pedants cares about the distinction. The thing that gets the electricity from the source to the vehicle is the charger; part of it is offboard the vehicle and part of it is onboard the vehicle. I can sometimes be pedantic in my own writing, but I don’t care which term you use. I purposely used the term “Charger” in the title because EVSE isn’t as commonly understood.
I hope others will add their own reviews of their chargers to this thread too.
I do want to first go over some terminology that does matter. I will use North American standards since Scout’s target audience is North America. This will be math-heavy:
Okay, this first post is long enough. I’ll put my first review in the next post.
I hope others will add their own reviews of their chargers to this thread too.
I do want to first go over some terminology that does matter. I will use North American standards since Scout’s target audience is North America. This will be math-heavy:
- Watt hours (Wh) = Energy
- Generally when discussing EVs, we use kilowatt hours (kWh).
- 1000 Wh = 1 kWh
- A battery holds potential energy measured in kWh
- An EV uses up energy measured in kWh
- Watts (kW) = Power
- This is the rate at which energy is used
- An EV draws power from the charger at a rate of kW
- Amps (A) = Current or flow rate of electrons through a circuit
- Volts (V) = Electric potential (how much pressure is measured between two electrically-active points of interest)
- Amps * Volts = Watts
- Example: A 50 Amp, 240 Volt outlet can allow up to 12 kW of power to flow
- 80% or 125% rule
- The National Electric Code requires that “continuous” (3 or more hours) loads be on a circuit that’s rated for 125% of the load
- Alternatively, you shouldn’t be pulling more than 80% of a rated circuit for a continuous load.
- Example: A circuit that’s rated for 50 amps is allowed to provide continuous loads of up to 80% of that rating, or 40 Amps
- The National Electric Code requires that “continuous” (3 or more hours) loads be on a circuit that’s rated for 125% of the load
- Charging time: If you divide the amount of energy (kWh) you want to add to your vehicle by the rate (kW) at which you add that energy, you can calculate the charging time.
- Example: A 100 kWh battery charging at a rate of 1.4 kW would take 100/1.4 = 71.4 hours to charge from 0% to 100%
- Example: A 100 kWh battery charging at a rate of 11 kW would take 9.1 hours to charge from 0% to 100%
- Example: A 100 kWh battery charging at a rate of 19 kW would take 5.3 hours to charge from 0% to 100%
- Example: A 100 kWh battery charging at a rate of 150 kW would take 40 minutes to charge from 0% to 100%
- Example: A 100 kWh battery charging at a rate of 200 kW would take 30 minutes to charge from 0% to 100%
- Level 1 charging:
- Using 120 volts, like from the standard 3-prong wall outlet.
- This is limited to 16 Amps maximum by the standards developed by the industry.
- 120 V * 16 A = 1.9 kW
- More common is 12 A because of the 80% rule: Your standard outlet is on a 15 A circuit, and the 80% rule means the charger shouldn’t pull more than 12 A from it.
- 120 V * 12 A = 1.44 kW
- Charging times are long. You use this when you need to recover your commute, but don’t need to recover from a long trip right away.
- Level 2 charging:
- Using 240 volts, like from an old dryer outlet or an electric range outlet
- This is limited to 80 Amps maximum if the vehicle has two onboard chargers (this is where the distinction between EVSE and charger matters)
- More common is 48 Amps or less
- Some examples:
- 240 V * 80 A = 19.2 kW
- 240 V * 48 A = 11.5 kW
- 240 V * 40 A = 9.6 kW
- 240 V * 32 A = 7.7 kW
- 240 V * 16 A = 3.8 kW
- 240 V * 12 A = 2.9 kW
- The slowest Level 2 charging is at least twice as fast as the most common Level 1 charging.
- Level 3 is misunderstood.
- In the standard, Level 3 is > 20 kW of AC power and generally is three phase power, which most homes do not have.
- A LOT of people, including automotive writers use "Level 3" to mean Direct Current (DC) Fast Charging (DCFC), which is a beast you won’t find in most homes, so I won’t discuss this here.
Okay, this first post is long enough. I’ll put my first review in the next post.